想取代现有的古董3管fin radiators in my old house but I’m not sure how many BTU’s per foot they produce.
Attachment shows 2 tube, 3 tube, and 4 tube (I’m not even sure what this style is called). I have the 3 tube arrangement throughout the house and I would like to be confident that when I upgrade, I’m getting more heat for each room in this 1650, modestly insulated, house.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
James,
If you take off the cover and examine one of these radiators, do you see any marks to give you a clue? Perhaps a manufacturer's name?
Those are the innards of cabinet type convectors. As shown in the picture they are rotated 90 degrees from how they sit in the enclosures.
If you measure the height & widths of the fins, and count the number of fins, and measure height & width of the enclosure they were in you can probably find a spec on a similar convector product. eg:
http://www.modinehvac.com/web/products/commercial-hydronic-equipment/convectors.htm
http://www.modinehvac.com/web/file?uuid=7ca61f5e-5554-4379-be2c-594b981a4614&owner=b7c1a0f1-c044-4ee5-aa41-9587d4a229d0&contentid=4026&name=AIR13-111.3_Convectors%2C_Technical_Manual.pdf
They are often specified for 215F steam and 200F entering water temperature (EWT), but the output can be inferred at other water temps:
At 180F EWT the output is about 80% of what it is at 200F EWT...
...at 140F EWT it's about 40% of the 200F EWT output spec...
... at 125F EWT (a good condensing boiler temp) it's about 25% of what it puts out with 200F EWT