Randy Mason| Posted inEnergy Efficiency and Durabilityon

I am replacing my existing siding and I am doing the following -stud – 5/8″ plywood – 1-1/2″ of Polyisol, 3/8″, WRB, rain screen, fiber cement siding. The house is in the San Francisco bay area on a hill with a stepped foundation.

I plan on putting a galvanized metal flashing were the bottom of the plywood meets the foundation (the rigid foam board will be slightly above the metal flashing). I have read numerous articles on this in regards to a horizontal run, but have not found one with details for a stepped foundation. I am assuming that the metal flashing should also run vertically. Should the metal flashing extend beyond the bottom of the fiber cement siding, or just up to it, or just before it? Have any of you had experience with this detail? Any suggestions?

Thanks,

Randy Mason

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Malcolm Taylor||#1

    Randy, The steps are best covered with trim rather than flashing. You could use wood or something like Anzec. What are you using for corners? The step detail should look the same.

  2. Randy Mason||#2

    Thanks for responding Malcom. I will probably use Anzek or a similar product for the corners of the house. So if I follow your approach - I would use metal flashing on the horizontal run and a trim piece on the vertical run. So the detail I need to worry about is any water that collects on the horizontal flashing can't flow to the top of the lower step trim piece. The easy way to do this would probably be to slightly tilt the horizontal metal flashing towards the next up step in the foundation. And I assume that I would leave no gap between the vertical trim piece and the foam board so that no debris or insects get in - in fact I am assuming I would want to make this as a tight as seal as possible?.

  3. TJ Elder||#3

    Randy, this is not to your question, but normally the WRB goes below furring strips, not on top. Also if your furring is only 3/8" would you be nailing the siding clear through the polyiso? Better to use 1x furring (3/4" thick) and then shorter nails, with siding attached only to the furring. Thin furring (3/8") would not effectively hold siding nails.

    As to the flashing, you could snip the first and third legs of the zee profile and then bend the flashing, so it follows the step at the foundation. Then just butt the siding up against the vertical leg, or leave a slight reveal.

  4. Expert Member
    Malcolm Taylor||#4

    Randy,
    I guess this ties in with my response to your other thread. I wouldn't use horizontal flashing at the base, but rather perforated U flashing.
    每当你使用类似闪烁,如the heads of windows, the best practice is to include end dams to stop water getting around the edges.
    http://www.ravenmetal.ca/installguide/rm1.5.html

  5. Randy Mason||#5

    TJ,

    My error in the original post - the WRB is going over the Rigid foam. I am using cor-a-vent sturdy strips for furring strips- so I will nail the siding through the rigid foam ( I can't use 1 x 4 furring strips due to exterior space limitations - a deck)