GBA Logo horizontal Facebook LinkedIn Email Pinterest Twitter Instagram YouTube Icon Navigation Search Icon Main Search Icon Video Play Icon Plus Icon Minus Icon Picture icon Hamburger Icon Close Icon Sorted

Community and Q&A

HRV delivering treated air directly to the ASHP air handler air intake which distributes cool or warm air through ducts

Susan Cosentini| Posted inGBA Pro Helpon

Has anyone tried this? The baths and kitchen would have dedicated exhaust fans.
This would in net-zero homes.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. D Dorsett||#1

    The air volume rates of heating air handlers (even mini-split mini-duct cassettes) is several times that of HRV/ERV units, and when you have competing air handler drives it un-balances the HRV flows, decreasing it's as-used performance.

    If you want the mini-duct cassette to help distribute ventilation air, putting an HRV supply register close to (but not connected to) the return air register of the mini-split cassette will achieve that modest increase in ventilation air mixing & distribution.

  2. GBA Editor
    Martin Holladay||#2

    Susan,
    I don't recommend the approach you are suggesting. By far the best approach is to have dedicated ventilation ducts for the HRV (completely independent of any ducts used for delivering space heat or cooling).

    For more information on the issue, seeDucting HRVs and ERVs.

Log in or create an account to post an answer.

Community

Recent Questions and Replies

  • |
  • |
  • |
  • |