Roof insulation / decking combination

Mike Gagne| Posted inEnergy Efficiency and Durabilityon

Hello, I live in Winnipeg MB, Canada (Zone 7, North of North Dakota).

I am insulating my garage ceiling to R22+ (standard pink fibreglass between 2×8 ceiling joists). I am also looking to insulate my garage roof to keep some of the heat from the summer out of the attic space in which I will store some things that i do not want subjected to high attic temperatures (I also expect this will help keep the garage cooler as well since the attic will be only about as hot as the outside air at most.

I intent to layer the system as follows:
1. OSB as the roof decking
2. 3.5 inches of XPS foam board
3. vertical 1x3s fastened through the foam
4. OSB over the 1x3s
5. 30lb felt
6. vertical 1x3s then horizontal 1×3 battens
7. Metal sheets

I know this seems overkill, but I am looking to ensure the top layer of OSB has airflow between it and the foam, and to ensure airflow under the metal sheets.

My intent is to keep this small attic cooler in summer, thus keeping the garage a bit cooler overall. But to be clear, the attic is unconditioned space with normal ventilation from soffits and ridge venting (so the OSB sheathing drys inwards if it ever has to dry at all) and during the winter the temperature in the attic and outside the garage will be the same so my intent has nothing to do with winter-time insulation.

Do you see any particular issues with this? Mostly I am concerned about degradation of the metal roofing but I cannot see any real buildup of moisture anywhere unless I am missing something.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay||#1

    Mike,
    All of the layers that you are planning above the roof sheathing are fine; in fact, it is an unusually robust assembly -- especially for an unconditioned garage. Assuming that you can afford these details, you should proceed with your plan.

    This type of roof assembly (with rigid foam above the roof sheathing) normally does not get a ventilation channel under the lower level of OSB. If you want to include soffit vents and ridge vents, these openings should be connected to the gap between the top of the rigid foam and the upper layer of OSB, rather than the attic space. That way, if the garage is ever conditioned, your soffit vents and ridge vent won't be undermining the effect of your foam insulation.