我们有大约13英寸的3翼砖负荷墙

我们没有在砖墙上进行任何隔热材料,而是在建筑检查员提出的框架计划时遇到问题。我们住在明尼苏达州。我们已经与这座城市作战并赢得了一场战斗,因此我们不必隔离,因为在这里冻结了融化的周期,因此人们担心砖的失败。

现在,我们的麻烦是与检查员的框架问题。我们的计划是使用砖块中附着在3英寸宽的嵌入式余烬上的现有毛茸茸的条。大多数人仍然处于机智状态,非常坚固。我们的计划是将石膏板连接到毛圈条上,但是检查员担心露点和由于凝结而变得潮湿。

The only change that we are making is that we have removed the lath & plaster and are adding 1/2 drywall. Does anyone have any experience with this? The inspector has concerns about where the dew point is, and how it has changed now by removing the plaster….. If anyone has any advice or information I am all ears. We have been battling them for almost 3 months now and we just need some resolution.

GBA Prime

加入建筑科学专家的领先社区

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

答复

  1. GBA Editor
    马丁·霍拉迪(Martin Holladay)||#1

    Kristina,
    As long as the building is heated in winter, the drywall will be close to room temperature, and will therefore be warm and dry -- just as the plaster used to be.

  2. 克里斯蒂娜·贝德尔(Kristina Beedle)||#2

    是的,建筑物将在冬季加热。我认为干墙的温度以及将传递给砖的热量与石膏的温度大致相同。

  3. Expert Member
    Michael Maines||#3

    克里斯蒂娜(Kristina),如果您绘制墙壁的缩放范围,则可以帮助您的检查员了解墙壁上发生的事情,如下所示。在外侧,画一条表示室外温度的水平线。高出它几英寸,在墙壁的内侧画一条水平线,代表70°或任何您喜欢的东西。通过连接水平线的墙壁画一条线。这是墙壁内的近似温度梯度,并清楚地表明,只要内部加热,干墙就会变暖。

    文件格式
  4. Trevor Trainor||#4

    Kristina,

    I think your inspector has a point. The issue is not the temperature of the drywall, but the temperature of the interior surface of the brick wall and the ability of vapour and interior air to reach it and condense within the wall assembly. What are the air and vapour control layers? When you apply the drywall to the furring strips, will this create an air gap? The change you are proposing could result in a significant change in the vapour and thermal profile of the wall and present condensation risk.

    我不会这么快地排除绝缘选项。如果与外部水控制措施合作正确地完成,则可以在不增加冻结/融化风险的情况下添加内部绝缘材料,并在此过程中创建更节能的房屋。约翰·斯特劳伯(John Straube)博士可以比我更好地解释这一点 - 查看有关该主题的论文 -

    http://www.buildingscience.com/documents/digests/bsd-14-interior-unsulation-sunsulation-Retrofits-of-load-load-boarning-masonry-walls-in-cold-climates/

    Trevor

  5. 克里斯蒂娜·贝德尔(Kristina Beedle)||#5

    I have actually been in contact with the Building Science corp, and because of the type of brick and the evidence of freeze thaw cycles in our paraphets we will not be insulating the walls. I have had several engineers and an architect advise against the insulation for our walls. All of the exterior items on the home have been addressed. Yes there will be an air gap and yes our plan is to attach the drywall right to the furring strips. They are very secure and have withstood the last 120 years. We will not be adding a vapor barrier as this would cause condensation between it and the brick, and we need the brick to breathe. We are proposing some sort of a ventilation system to help control the moisture, but I just don't see how drywall would allow or add any more moisture than the lath & plaster did...as there was an sir gap with the lath & plaster too.

  6. GBA Editor
    马丁·霍拉迪(Martin Holladay)||#6

    特雷弗,
    You have it backwards.

    You wrote, "The change you are proposing could result in a significant change in the vapour and thermal profile of the wall and present condensation risk."

    实际上,如果没有隔热材料,则砖块将变暖,烘干机,如果安装了隔热材料。

  7. Trevor Trainor||#7

    Sorry to be unclear. My point was that by removing the stucco and replacing it with drywall, you will be changing the vapour and thermal profile of the wall. If there was an air gap previously, then the change in the thermal profile will be minimum, but the vapour permiability of drywall is approximately 5 times higher than stucco, changing the vapour profile significantly. The other issue to consider is the moisture tolerance of drywall compared to stucco. Condensation moisture touching the stucco in the old wall system would not cause damage, while it only takes a small amount of moisture to cause problems with drywall.

    You just want to make sure that you do a really good job of controlling air and vapour flow from the inside in this low R wall system.

  8. Expert Member
    Michael Maines||#8

    The original plaster likely had many coats of relatively impermeable oil-based and/or lead paint. The new drywall (installed over existing furring strips, according to Kristina) will likely be covered with permeable latex paint.

  9. GBA Editor
    马丁·霍拉迪(Martin Holladay)||#9

    迈克尔和特雷弗,
    While you are right that the vapor permeance of the drywall may differ from that of the painted plaster, (1) it's an easy matter to apply a coat of vapor-retarder paint to the drywall, and (2) my original point -- that the drywall will stay warm and dry all winter as long as the building is heated -- remains true.

  10. 克里斯蒂娜·贝德尔(Kristina Beedle)||#10

    感谢大家。感谢您的意见。