Attic condensation
我最近在我的Cape Cod风格阁楼中发现了一个冷凝问题,我遗憾的是最近完成了重新绝缘。我住在鲁珀特王子,BC(靠近阿拉斯加州),在5/6区的边境北部BC海岸。相当温和,海洋气候。
I furred down the existing 2×4 cathedral rafters with a 2×4 for a rafter depth of 7″ and installed a 1 1/2″ vent chute using R5 ridgid foam (spray foamed in place), then filled the remainder of the cavity with R22 Roxul for a total of a little less than R28 since the batt was compressed an inch. Ideally I would have furred down the rafters further to create a deeper cavity to insulate, however, I also had headroom issues to deal with. Kneewalls were insulated with R22 roxul and the floor joist area behind the kneewall was insulated with approx R50 blow-in fibreglass with ridgid foam blocking between joists below the kneewalls. I was able to get close to R50 with the blow-in insulation right to the exterior wall, since the rafters oddly ran right out to the soffit, not sitting on the exterior wall, so I framed a small pony wall supporting the rafter above the exterior wall. The walls and ceilings in the attic all have a 6mil vapour barrier installed as per our code requirements in BC. The main floor ceilings below do not have a vapour barrier installed as far as I can tell and are a mix of fibre-board ceiling tiles, lathe and plaster and drywall depending on the room.
I’m also in the process of re-doing the old cedar shake roof, stripping off the cedar shakes, sheeting with 1/2″ plywood and installing asphalt shingles. Half of the roof is currently completed.
We’ve recently had some cool weather, down to approx -5C and shortly thereafter, I noticed staining on the living room ceiling tiles and my first thought was a roof leak as it was on the side of the roof not yet fixed, however, after going into the attic I discovered that it wasn’t a roof leak, but the underside of the roof appears to be either iced up, or wet, which would suggest heat loss. This is on the underside of the roof, both behind the kneewalls above the blow-in insulation and from what I can see, continuing up the underside of the roof into the vent chute cavities as well. My suspicion is the heat loss is getting up through the blow-in insulation and continuing up the cathedral ceiling, since I don’t know how the heat loss would be occuring through the cathedral ceiling itself(vapour barrier, Roxul and air sealed vent chute). This condensation issue seems to be consistent between all areas of the attic regardless of the room(ceiling type) below. The attic was initially insulated with a small amount of R12 fibreglass batts and vermiculite and didn’t appear to have any condensation issues. Any thoughts/suggestions would be appreciated. Thanks in advance.
泰森霍普金斯
鲁珀特王子,BC
GBA详细资料库
由气候和房屋部件组织的一千个建筑细节的集合
这可能是水分迁移的问题nd air leaks more than a problem of “heat loss” through the insulation. It looks like you have frost on the nails coming through the roof sheathing.
我怀疑以下之一:
1-在进行空气密封工作时,您错过了一些东西(在安装绝缘之前,您在安装绝缘之前的空气密封)。我会检查顶板,特别是电气和管道穿透。这是我自己的房子里造成同样的问题。
2- you have something leaking, or a bathroom or dryer vent located in such a way that a portion of the moist exhaust air is getting into one of your soffit vents and entering your attic.
3- you don’t have enough attic venting (this is a last step or a band aid if 1 and 2, above, can’t be fixed).
账单
我很遗憾地说这一点,但真正的问题是某人建造了一个故事和半房子,本质上几乎不可能将暖气保持在房子内。下一个问题是有人买了它并试图改善它。
您可以在魔鬼三角形上找到有用的文章。
//m.etiketa4.com/question/devils-triangle-updatehtptps://www.greenbuildingadadadadoadvisor.com/article/Insion-aa-cape-cod-house.
在我看来,您需要将您的房屋空气密封到不到2个ACH50。这几乎肯定需要您删除新的删除新的保温,如果您无法获得良好的鼓风机门测试,请勿将绝缘保留背部,因为您需要阁楼的热量保持干燥。
沃尔塔
If your ceiling is only ceiling tiles as you mention in your post, then that is your problem.
天花板瓷砖像筛子一样泄漏。你需要一个适当的空中障碍。吹蓬松的绝缘保温无需停止空气流量。
如果实际上是这种情况,如果来自阁楼的情况现在非常艰难。你必须耙开所有的保温,以某种方式(1英寸的喷雾泡沫封装是最简单的,你可能能够详细说明6米兰塑料,但它会很棘手)。