社区和问答

在地下地板下泡沫多少钱?

Nick Hall| Posted in一般的问题on

我正在努力确定在房子设计下放置多少泡沫,我有一个令人惊讶的艰难时间来提出明确的答案。这是气候区7,地面温度下降在40-45°F左右。大多数家庭在这里做2英寸的泡沫。我的房子设计是一个罢工地下室,所以房子的一侧会靠近地面,另外3侧是土壤约8英尺的土壤。ICF墙壁。

借助于墙壁的热量损失粗糙模型非常简单,例如:面积* U值*Δδ-T。But when I apply this same equation to a basement floor, if I use R-10 for the floor (~2″ of foam) and a ground temperature of 45F, even though the 45F temperature isn’t too far from the heating set point compared to being -20F outside, the basement floor ends up being quite a large contributor to heat loss — significantly more than the ceiling even though the ceiling is exposed to much colder temperatures.

但土壤不是散热器的空气,所以房子下面的地面不会持续45°F - 来自房子的热量会使土壤温暖并降低热量损失。但是多少?

I have been using BEOpt to model heat loss but there surprisingly isn’t an option for basement floor insulation. I found this thread on their message board:https://beopt.nrech.gov/node/124.基本上说他们不认为地下室的绝缘材料具有显着效果。

Also, if I’m reading the manual J guide correctly, I think they only factor in linear feet of perimeter around the slab to figure heat loss through the slab? And it seems like they figure it would be quite low.

所以我想知道 - 这已经研究过吗?在板块下将超过2英寸的泡沫帮助任何内容,无论是在减少热量损失或增加一个在板上行走时感觉的温度吗?我如何确定热量损失真正在2“的情况下,它是真正的R-10,或者有一些方法可以用于热损失方程的图形?谢谢。

GBA Prime.

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA编辑器
    Martin Holladay||#1

    Nick,
    你已经彻底的研究。简单地说,国防部eling heat loss through a basement slab is extremely complicated. Moreover, assumptions about this type of heat loss are controversial. PHPP software often shows higher levels of heat loss through slabs than energy modeling programs written in North America, and the discrepancy is unresolved.

    For a fairly thorough discussion of this issue, read this article (along with the 96 comments that follow):Can Foam Insulation Be Too Thick?

    还应该指出这个问题的答案严重依赖于您的能源成本。

    For a rough guide, I advise you to follow the advice of building scientist John Straube.

    Straube写道,“绝缘成本变得超过了在大约R-60(使用建筑科学公司方法)的7,200-HDD气候中为典型房屋中的墙壁产生能量的成本,以及平板[在等级]关于R-20至R-25,取决于放置EPS的成本(每平方英尺每平方米约10美分)。基础的热量损失较少[比等级上的板坯],因此截止点更像R-15至R-20,用于基底板。加热带辐射管的板坯将平板的温度从大约68°F或其平均增加到80°F,因此绝缘水平需要增加约50%的辐射加热的板坯。“

    其他专家曾使用其他计算方法来提出建议,以便在基底板下的低于绝缘水平的建议。例如,Gary Proskiw和Anik Parekh已经计算出即使在Yukon领域的黄刀中,基底板也不需要在板坯周边处的R-10垂直绝缘。可以在此处找到完整的详细信息:Optimization of Net Zero Energy Houses

    Finally, the main reason to install at least 2 inches of rigid foam under a basement slab in your climate zone has nothing to do with saving energy. The main purpose of the rigid foam is to make sure that the slab stays warm enough to prevent condensation. This will (a) make your basement smell better (because it won't be damp or moldy) and (b) make your slab warm enough to allow you to install carpeting if you want to, without worrying that mold will grow under the carpeting.

  2. Bob Irving||#2

    "the heat from the house will warm the soil and reduce the heat loss." Not quite.
    If you build a well insulated slab, you can raise the temperature of the slab by adding heat, but the soil under your house is thousands of feet deep, not a few inches, and the temperature never changes, so the heat you deliver to the sub-slab soil will be transferred to colder soil in an ongoing process. Your insulated frost walls at the walk out will help with slab temperatures. 4" of EPS (minimum) will give you about R16; 6" will give you R24.

  3. Expert Member
    Dana Dorsett||#3

    The soil under the slab has both R-value and thermal mass, both of which vary considerably by soil type and moisture content, making the modeling complex. With the exception of active volcanic areas or flowing artesian water streams the temp of the soil 50-100' down is close to the average outdoor air temp over the past 50-100 years in the area. The temp several hundred or thousands of feet down is much warmer, due to the high core temp of the planet, but that temp is completely irrelevant to this discussion.

    分布式soil-R所以的时间常数il-mass over a season or at most a year is the relevant time period from a slab insulation perspective, and there we are talking a couple tens of feet down at MOST. The slab losses DO raise the temp of the proximate layers of soil, reducing both the rate of loss and the total loss from the slab. The more insulation you put under the slab the less the soil is heated, so the soil stays colder, and the thermal mass of the soil then has diminishing effects on energy use. Putting R10 down instead of only R5 doesn't cut the heat loss by half- not even close, and the difference between R10 and R20 sub-slab foam is even smaller.

    如果已知更多的局部土壤特性,这可以以更高的精度建模,但完全表征位点的土壤的成本超过加入更多英寸泡沫的成本。

    The amount of sub-slab R necessary to mitigate summertime mold and musty-basement issues is pretty modest- R5 -R6 (1.5" of EPS) would be fine even in zone 7. There's still a long term or lifecycle financial energy cost savings argument for R12-R15 or so even for basement slabs, and for on-grade slab edges even up to ~R20 in that climate, but not R25 (unless you expect future energy costs to be several times the levelized cost of solar electricity at today's PV prices.)

  4. 查理沙利文||#4

    上面的伟大答案。我补充说,因为接地温度比外部温度要温暖得多,因此地面的热量损失根据你保持空间的温暖程度强烈地变化,而不是通过墙壁的热量损失更强烈。所以如果你打算让地下室在冬天保持凉爽,你可能会选择一点;如果您计划完全调整它,更多。

    Definitely use EPS, not XPS--you get more insulation value per $, as well as much lower environmental impact.

  5. Nick Hall||#5

    Thanks for the responses!

  6. Brian P.||#6

    When planning (and during) our house build, I devoured as much information about other house projects as I could. Anecdotal evidence shows most low energy or net-zero builds in the Northeast US are using at least R20 under slab. Many up to R30 or more.

    4" of EPS seems like a safe choice (versus 2") if planning an energy efficient house in zone 7.

  7. GBA编辑器
    Martin Holladay||#7

    布莱恩,
    你没有告诉我们你是否正在谈论地下室平板或等级的平板。

    Nick: basement slabs can get away with much thinner sub-slab insulation than a slab on grade.

  8. Nick Hall||#8

    Yes, the slab I'm talking about is below a basement so under the frost line. Except for the edge by the walkout which is more like a slab on grade, but if I insulate the frost wall there does that make it perform more like a basement slab even at that edge? I'm wondering if I should just do the frost wall as ICF since the rest of the wall there will also be ICF?

  9. Brian P.||#9

    Correct, I was just offering some general insight into what I learned as a first time home builder/owner and I don't have a solid answer.

    如果尼克因犹豫不决而瘫痪,陷入困境,在建模/计算中陷入困境,并且需要作出决定在现场获取材料.....我想击中R15-20将是他局势的好处?