Insulation and mechanical plan critique for 115-year-old retrofit

Tom Woodson| Posted inMechanicalson

Currents State:
– Zone 4A (st louis). Heating design temp 10F / Cooling 93F
-1700 sq foot 2nd floor rental apartment
-3 wythe thick brick walls (12 inches)
-Low slope roof with 4 inches polyiso and TPO membrane
-Small “false” roof in front 5 foot high peak
-10 foot ceilings
-14 large (72″x34″) original windows windows (retrofitted with silicone and polypropylene seals, low-e storms)
– 1 5/8″ steel framing to the inside with min 1″ gap from brick.

Insulation Plan:
Wall – 1.5 inches of closed cell spray foam (Icynene ProSeal). Trying to balancing the risk of freeze/thaw damage risk and interior comfort/equipment sizing. Improved water management on exterior parapet, windows to keep brick dryer. Exterior parapet bricks were in good condition, so I’m not overly concerned.
Ceiling – R38 fiberglass batts between roof joists (4 inches of exterior poly already in place)
False Roof – 4 inches of spray foam on interior with R38 batts (framed out on inside to accommodate)

Mechanical Plan
-CoolCalc Manual J attached
-Careful Manual D done to ensure correct airflow/low static pressure
-Fujitsu 9RLFCD ducted mini-split for back rooms/bathrooms
-Fujitsu 18RLFCD for front kitchen, living rooms, front bedroom
-Panasonic WhisperComfort ERV
-Panasonic WhisperGreen bath fans

I know that I am slightly oversized, however, I was 1) concerned about undersizing for cold/hot snaps with tenants complaining. 2) concerned about airflow (the 1.5 ton unit can move more air)

File format File format File format

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Peter Yost||#1

    Hi Tom -

    Mechanical system sizing and calcs is not my strong suit but I can tell you that your concern regarding freeze-thaw for your climate: no worries. Even with making your 3-wythe brick colder with interior insulation, you should not have issues in your climate.

    Peter

  2. Tom Woodson||#2

    Thanks Peter, that may convince me to add a bit more insulation. It would be nice to have R20 walls and r60 ceiling.

    Any opinions about the depth of the foam on the walls? Can i decrease to 1 inch and add r8 batts to fill? That would get me about the same as 2 inches of foam and I'm guessing cost substantially less.