Is it a good idea to use foil-faced rock wool under the basement slab?

I will be building a new house in climate zone 5. I’m doing my best to achieve the R10-20-40-60 insulation level goal. I’ve been able to find some discount rock wool board that I would like to use below the concrete slab in the basement. Specifically 1″ thick Thermafiber Firespan 90. This has a 8.0pcf density which would be good for sub slab, however it also has a foil faced vapor retarder. I would like to stack 2 layers of the product to achieve an R8.4 value (close enough to the R10 goal).
The basement slab construction is as follows (from top to bottom):
4″ concrete with wire mesh
6mil vapor barrier
2″ of Rock wool insulation board
总为毛细管打破
Is it a good idea to use foil faced rock wool board under the slab?
Is it a good idea to stack 2 layers of the product?
I would think the top layer of foil which is in direct contact with the 6mil vapor barrier would be ok, however, I could see the lower layer being a problem. Thoughts?
Thanks-
Adam
GBA Detail Library
A collection of one thousand construction details organized by climate and house part


Replies
Adam,
The foil facing won't cause any problems in this application.
You should be aware, however, that there are a few caveats to remember when using mineral wool under a slab: some local building inspectors may not approve the method, and you can't use mineral wool under footings. For more information, seeSub-Slab Mineral Wool.
Adam,
I suppose that in rare conditions -- if there is rising groundwater and a simultaneous failure of your footing drains -- the intermediate foil might trap some liquid water.
If this unlike scenario worries you, you can pierce the foil facing with a wrecking bar -- punching a few holes in each panel of insulation -- as you install it.
Good suggestions Martin. Thank you once again for your prompt reply. I will plan on puncturing the lower layer of foil, and proceed as planned. Also Ill check with the county building inspector if they allow this product sub slab.