Mini Split Equipment Selection Zone 3A

I’ve been going in circles trying to choose a mini split system to replace my 36(!) year old heat pump. Would love a little sanity check or guidance from some of the brilliant minds here regarding sizing. Also interested in opinions on whether I should even be looking at Hyper Heat units & particular model recommendations in regards to their modulation ranges.
The house will be about 1,475 sq ft after a planned 270 sq ft addition. Single story, built 1984, vented attic with very little insulation, vented crawl space, north Alabama climate zone 3A. I’m going from a packaged 2 ton heat pump that’s falling apart with terribly leaky ducts in crawl space to a Mitsubishi mini split with air handler(probably SVZ) in hall closet, new ducts in attic consisting of two straight, similar length trunks & several straight branches. I will be doing considerable air sealing & insulation in the attic.
I did a Manual J, including the room addition & got a heating load of 31,627 BTUH, sensible cooling load of 24,456, latent load of 3,435. This would seem to suggest something like the SUZ-KA24 or even SUZ-KA30. But am I right in thinking that’s a little over-sized given my current configuration? Granted, the current unit struggles to keep up at times, but I would assume that has more to do with it’s age & condition than anything else.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part


Replies
Not having the ducts in the vented attic would be better. That said, 2.6 tons doesn’t sound oversized (but that’s a WAG). Zone 3A is pretty mild heating-wise, so I don’t know why you would need a hyper heat modal.
Can you provide more detail about your structure? Can you upload your Manual J?
Yes, I know ducts inside the envelope would be better, but this is what I have to work with. I couldn't see much use in the Hyper Heat either, honestly it was a comment by Allison Bailes over at Energy Vanguard that made me wonder if I was missing something there. I'll attach my Manual J.