Roof insulation plan — low slope — trusses
Prior roof questions — //m.etiketa4.com/question/roof-insulation-plan#comment-146956?utm_medium=email&utm_source=notification&utm_campaign=comment_notification&utm_content=view
Climate Zone 5 – low slope roof –
most of the roof is cathedral – 12″ I-joists – flash and batt (fill- with BIBS) approach. From areas that use trusses and the interior ceiling is flat, do you do the same thing? (flash and fill – foam on undersurface of the roof deck with BIBS suspended below it). We would still use an unventilated assembly.
Thanks,
Alan
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Alan,
The image that you attempted to upload didn't work. (That problem may be due to a site glitch on GBA -- I've had the same problem recently. I hope the problem is resolved soon.)
If you use the flash-and-fill approach for your low-slope roof, that doesn't mean you have to use the flash-and-fill approach everywhere. But for the roof assembly that has a horizontal ceiling, I'm not sure what type of attic you have above the horizontal ceiling. You wrote that this assembly with a horizontal ceiling would still be "unventilated" -- and I'm not sure why, if there is an attic above.
Martin - the slope is 1.5:12. There is only about 11" for an air space and insulation where the roof meets the exterior wall. I didn't think there is enough room to ventilate it. I also thought the low slope has inadequate vertical difference to get air to move through an air/vent without a dog house on the roof - something we would like to avoid.
Is my understanding of this inaccurate?
Thanks, Alan
Alan,
For the portions of your house with a horizontal ceiling, it would be safer to keep the flash-and-fill insulation along the roof plane, not against the horizontal ceiling. Otherwise, there is a risk that you'll get moisture condensing on your cold roof sheathing.
Without any attic ventilation, this risk increases. All it takes is a few air leaks for your roof sheathing to be in trouble.