Are there any issues with Spray-foam next to Batt insulated walls?

Martin Brown| Posted inGreen Building Techniqueson

We have a project where we there are additions and renovations to an existing residence that has batt insulation throughout. We have specified closed cell spray foam insulation to be used in the addition walls floor and sloped ceilings and batt in flat ceilings. In the existing part of the house where some exterior walls will be renovated we have specified spray-foam. The remaining existing house will not receive new insulation. My questions is, are there any issues with condensation using both insulation types adjacent to each other? A spray foam contractor has brought this up, but I can not find any research on this.

Thanks

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Dana Dorsett||#1

    There are no inherent issues with condensation with foam in one stud/rafter bay and fiber in another. In general the foamed part of the assemblies will be more air-tight than the fiber-insulated assemblies (unless there was significant air-sealing detailing on the fiber-insulated parts.)

    Making the whole house more air tight raises the humidity levels inside an occupied house, but that is independent of the insulation, and needs to be monitored & controlled in any tight house. If it's staying well above 35% RH @ 70F indoors even during a week of weather where the daily high temps never break +20F, mechanical ventilation (preferably a heat or energy recovery type) under dehumidistat control keeping it at 30-35% RH would be a good idea, which would lower the risk of moisture buildup in the sheathing of the fiber-insulated part.

  2. Martin Brown||#2

    Dana, Thank you for your assistance...this was very helpful