GBA Logo horizontal Facebook LinkedIn Email Pinterest Twitter Instagram YouTube Icon Navigation Search Icon Main Search Icon Video Play Icon Audio Play Icon Headphones Icon Plus Icon Minus Icon Check Icon Print Icon Picture icon Single Arrow Icon Double Arrow Icon Hamburger Icon TV Icon Close Icon Sorted 汉堡/搜索图标

Community and Q&A

Bathroom exhaust duct

E247| Posted inGeneral Questionson

I have a conditioned attic and I wanted to know if the bathroom exhaust ducts need to be insulated. There’s a backdraft damper on the roof termination and at one built into the fan.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay||#1

    E247,
    First of all, can you tell use your name? (I'm Martin.)

    Q. "I have a conditioned attic and I wanted to know if the bathroom exhaust ducts need to be insulated."

    A. The answer depends on your climate zone. If you've got a very short duct run that passes through roof insulation and ends in a roof termination, your duct is obviously already insulated.

    For more information, see"Bathroom Exhaust Fans."

    1. E247||#2

      Climate Zone 2A. One run is about 6' from the fan to the roof termination and the other is about 20' from the bath fan to the roof termination. There is spray foam against the roof deck so most of the duct isn't insulated.

  2. GBA Editor
    Martin Holladay||#3

    E247,
    If the 6-foot length of duct is in conditioned space -- and it sounds like it is -- then the duct doesn't need to be insulated.