如何密封比尔科门以防止热量损失和潮湿的空气转移?

贾斯·瑟伯(Jas Thurber)|发布GBA Pro帮助

我们有一个标准的Bilco门,可在我们的地下室中半整合空间。在冬季,我们在冷空气中遇到麻烦,并在春季/夏季潮湿的空气潮湿。我们如何在门周围和/或密封周围造成凝结问题而不会造成凝结问题?空气来自门口的裂缝铰链和门上。看来Bilco外壳单元已正确密封到混凝土。Home Depot出售覆盖门的聚碳酸酯圆顶。我考虑过沿圆顶的底部边缘进行一条天气剥离,为夏季的几个月中创建了圆顶的印章,但不知道这是否可以解决问题。我假设圆顶在冬天无济于事。我考虑过将一块刚性泡沫板放在通向地下室的比尔科楼梯的底部,因为在底座上有一个由2x4制成的门口框架。但是,我想知道我是否会在比尔科门侧遇到冷凝问题? I also don’t love XPS board. I know that it off-gasses and our basement also has finished space where the kids play. I do have a roll of Dennyfoil vapor barrier that I could wrap the XPS board with I suppose. The basement room that the Bilco opens to is insulated with standard batt fiberglass (but no sheet rock). It is framed off from the mechanical room (also insulated, with no sheet rock) and finished space. There is a standard door that leads to the finished space from the Bilco room. Any suggestions would be greatly appreciated. Thanks!

GBA Prime

加入建筑科学专家的领先社区

成为GBA Prime成员,并立即访问该领域的绿色建筑,研究和报告中的最新发展。

答复

  1. 丹·科尔伯特(Dan Kolbert)||#1

    您将在基础墙上建造自己的绝缘门时,您将有更加容易的时间。

  2. GBA编辑
    马丁·霍拉迪(Martin Holladay)||#2

    贾斯,
    丹是正确的。空气密封发生在安装在楼梯底部的门上,而不是在钢舱门门处。

  3. 比尔科公司||#3

    这是正确的答案。Bilco建议在楼梯底部使用绝缘垂直门,以提高能效和增加的安全性。室外金属表面总是会在底面上获得极其热和凉爽的地下空气,将产生冷凝水。Bilco品牌的门被设计为Weathertight,但是故意设计的,上面有气隙。这使金属门两侧的温度平衡以消除冷凝水。