I am insulating my cottage

拉里Rummel|发布General Questions

I am insulating my cottage. I need to know if I need to seal all the cracks completely in the outside wall? It is wood Dutch Lap siding.

I want to use 2″ blue extruded (XPS) board, and 4″ fiberglass insulation with vapor barrier, for a 6″ wall. And also, what about the seams in the 2″ foam boards? The interior wall will be 1/4″ OSB with knotty pine 1/4″ paneling. Is the vapor barrier on the fiberglass enough?
拉里

GBA Prime

加入建筑科学专家的领先社区

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay||#1

    拉里,
    Every wall needs at least one, and sometimes two, air barriers. For more information on this topic, seeQuestions and Answers About Air Barriers.

    It's unclear from your question whether the rigid foam will be installed on the exterior side of your wall or the interior side of your wall.

    It's also unclear whether you are talking about new construction or retrofit work. If it is retrofit work, are you opening up the wall from the interior or the exterior?

    如果您的墙壁上有OSB或胶合板护套,并且如果您可以进入护套接缝,则可以通过用高质量(通常是欧洲)胶带密封接缝来创建空气屏障。

    面对玻璃纤维板上的牛皮纸不是空气屏障。

  2. Expert Member
    Dana Dorsett||#2

    A true vapor barrier on the interior side of a wall with 4" of cavity fiberglass and 2" of exterior XPS is risky due to the fairly low vapor permeance of XPS at that thickness (about 0.5-0.7 perms.)

    In most climates the ~2 perm vapor retardency of the interior OSB layer (if made air-tight) would be plenty. If you used half-inch OSB instead of 1/4" you'd be at about 1 perm, a bit less when you add in the vapor retardency of the 1/4" pine paneling, which would be fine.

    In most US climates R10 on the exterior of R15(?) fiberglass would be sufficient for dew point control at the sheathing even with 5-perm paint on sheet-rock as the interior vapor retarder.

    Kraft facers on batts are variable permeance, about 0.4 perms when dry, 5+ perms when wet, but it's probably better to do without them. Air tightness is going to be the most critical thing here, but try to leave yourself about 1 perm, not a lot less, or the very slow drying rates can impact moisture resilience.

    Also, if the true depth is 4", as with rough-cut full dimension 2x4s, and not the 1.5'x 3.5" dimensions of a milled 2x4, fitting batts correctly is going to be a problem. The widths may need to be sculpted & trimmed to keep them from buckling, forming depressions & voids, and you'll have to use a thicker batt than an R13 or R15, since the manufactured loft is less than 4". Using low density R19s or R22s designed for 2x6 framing can be made to work, but it's a bit of a pain. Blown insulation is a better solution when using full-dimension framing lumber. An R19 compressed to 4.0" will run about R15-R16:

    //m.etiketa4.com/sites/default/files/Compressing%20fiberglass.jpg