Insulating a sloped open space
How would one place cellulose in a large 2′ tall sloped (4:12) under roof space with a smooth sloped floor and ceiling and no internal framing? Assume that ventilation is taken care of elsewhere. My biggest concern is keeping the insulation where it belongs.
–John
John,
You haven't provided a clear description of this space, but here are the relevant principles:
1. Unless this roof assembly includes an adequately thick layer of rigid foam above the roof sheathing, building codes require that you include a ventilated air space between the underside of the roof sheathing and the top of the cellulose insulation.
2. If the cellulose is going to be installed in a sloped roof assembly, then you need to encapsulate the area before blowing in the insulation. If these are deep rafters, then you would need to install site-built ventilation baffles to enclose the insulation at the top, and some type of material -- InsulWeb, drywall, or rigid foam -- on the underside of the rafters to enclose the insulation at the bottom.
Here are links to two relevant articles:
Site-Built Ventilation Baffles for Roofs
How to Install Cellulose Insulation