Envelope Details for Converted Stucco Garage

StephanieHerynk| Posted inGeneral Questionson

Hello,
Advising on the conversion of a stucco clad garage (1960’s-1980’s?) into a conditioned living space. The budget does not allow for the stucco to be replaced and an air gap added. Thus I’m looking for advice on how best to advise a workable conversion to living space that remains fairly economical.
Please see attached images and details below.
Thank you in advance for your input!
– Stephanie

Existing Conditions:
– Stucco
– Presumed concrete board? I don’t see any tar paper or mesh..
– Plank sheathing
– 2×4 framing
– No insulation
– Unconditioned garage space

Proposed Conditions:
– Stucco
– Presumed concrete board? I don’t see any tar paper or mesh..
– Plank sheathing (mold areas to be treated)
– 2×4 framing
– Mineral wool batt insulation (suggested this over fiberglass due to potential moisture in the wall, and fiberglass losing r-value when wet. Spray foam was voted out. Thoughts? Is mineral wool overkill and they could get by with unfaced fiberglass?) R-13
– Drywall (should this be paperless since there is evidence of moisture on the plank sheathing?)
– Client to add heating (and maybe AC, or at least a fan) via a minisplit or electric panel/base heat.
– Concrete slab to be poured. Suggested adding EPS foam below slab, and/or sealing the surface.

My primary questions/concerns are:
– What is the recommended assembly for these conditions?
– Would it be catastrophic if the client were to go ahead with fiberglass and regular drywall?
– I believe the wall would dry in both directions either way… but I’m worried about where the dewpoint will fall with the added insulation/conditioning.

Thank you again for any and all input

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. StephanieHerynk||#1

    Anyone available to advise?

    1. Expert Member
      Malcolm Taylor||#2

      Stephanie,

      I would treat this the way you would a structure without sheathing. The details in the links below would allow the cladding and board sheathing to dry, while limiting water intrusion.

      //m.etiketa4.com/article/managing-water-and-insulating-walls-without-sheathing

      //m.etiketa4.com/article/insulating-walls-in-an-old-house-with-no-
      sheathing

      1. StephanieHerynk||#3

        Thank you Malcom. This is exactly what I was looking for -- multiple options. Take care!

        1. Expert Member
          Akos||#4

          There also looks like a fair bit of water damage on the bottom of the wall. You need to fix the source of this before insulating as it can create a lot of issues down the road.

          Maybe the grading outside needs to be lowered/sloped, gutters installed or downspouts direct away from the structure. The commonly seen planters against the garage wall are also a bad idea.

          1. StephanieHerynk||#5

            Hi Issac, thanks for chiming in!
            是的他们是解决水损害,corner. A combination of a downspout to who knows where (likely clogged), and the grade currently sloping towards that wall.