Open-cell spray foam under a flat roof

I am finally at the insulation stage on my drawn out renovation of a 1905 all brick 2 family. The roof already has 4 inches of polyiso above the roof deck with a TPO membrane. My foam contractor is recommending the following:
1) 2 inches (all that will fit) of closed cell foam to the walls and parapets.
2) 7-8 inches of open cell foam below the roof deck between the roof rafters. He is concerned that if there is ever a roof leak, the roof will rot as there will be nowhere for water to go. Makes sense to me.
Is this a good assembly? My calculation is that 4 inches of foam above will keep my sheathing from being at condensing temp.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part


Replies
Tom,
It would be helpful to know your geographical location or climate zone.
Four inches of polyiso has an R-value of about R-25. Eight inches of open-cell spray foam has an R-value of about R-30, so the R-value of your entire roof assembly would be about R-55, with about 45% of the total R-value in the form of vapor-impermeable exterior rigid foam.
Conservative builders would say that your suggested approach will work in Climate Zone 5 or anywhere warmer, but might be a little risky in Zones 6, 7, 0r 8. (For more information on this issue, see"Combining Exterior Rigid Foam With Fluffy Insulation.")
But since open-cell spray foam isn't air-permeable -- it's just vapor-permeable -- the risk is lower than it would be if you were planning to install fiberglass batts on the interior side of the roof sheathing. So even in a cold climate, you'll probably be OK.
Thanks Martin. I am in zone 4a (st Louis). Sounds like I have a plan. I love the idea of a foam bubble on this old house to seal it up.
Already have a Panasonic whispercomfort erv installed to provide engineered ventilation and I’m using the new Fujitsu mid-static ducted system for hvac. I’ll report back on the performance as soon as I get some data.