UA and Rescheck
Just ran a Rescheck. I like the software, simple and seems to be informative possibly for more than just getting a passing Rescheck to submit.
有更多的我可以学习报告listing of UA?
The software reports individual UA and total for the home.
Can one simply input these UA numbers into a formula to report BTU use per Delta T as Marc is doing in his great blog answering questions to do with mini split use?
Dana, Marc, Martin, others?
AJ,
The heat loss formula for determining transmission losses through floors, roofs, and walls is
Q = A • U • ΔT.
In other words, the rate of heat flow through a building assembly (in Btu/h) is equal to the area of the assembly (in ft²) times the U-factor (in Btu/ft² • hr • F°) of the assembly times the ΔT (in F°).
This is explained in my blog,How to Perform a Heat-Loss Calculation — Part 2.
UA (defined as the "overall average heat transmission of a gross area of the exterior building envelope") is used to measure whole-building heat loss in Btu/h°F.
Area x U-factor = UA
Multiply the surface area of each exposed component of the building envelope by its U-factor to get its "UA" value. Add up all the UA values to get a total building UA value.
Great. Thanks Martin