Community and Q&A

Adding interior insulation on a brick veneer house – Concern about inward solar drive caused moisture issues.

Joshua Van Tol.|发布了能源效率和耐用性

I own a 1929 brick veneer home and have been steadily improving the airtightness and insulation levels. The time has come to consider the exterior walls, which are (from inside to outside) plaster over celotex, 2×4 framing (hybrid balloon framing), ship lap sheathing, tar paper, 3/4″ air gap, then brick. The house is 2 stories, and has approximately 2′ overhangs. The walls currently have about 1″ of insulation in the form of some sort of prairie grass encapsulated in kraft paper, which is nailed in place with 1/4 wood strips.

In an ideal world, we’d tear out the exterior walls, insulate full depth with closed cell spray foam, and then re-install drywall, perhaps with a layer of rigid foam under the drywall to reduce thermal bridging and bring the wall thickness up at least to the original thickness so that baseboards and such can be re-fitted.

Should I be concerned about potential wetting of the sheathing and framing? I’m in a mixed/cold climate in south east MN.

或者,我还考虑低扩张的注射泡沫(虽然我没有找到承包商,但我尚未相信)或从内部安装的纤维素。

The alternate approaches have appeal because of the cost savings and because the existing plaster is in great shape.

GBA Prime

加入建设科学专家的领先社区

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
  2. GBA Editor
    Martin Holladay||#2

    Joshua,
    Have you read this article?绝缘老砖建筑

  3. Joshua Van Tol.||#3

    I've read the paper and the article. Both address solid masonry walls. I've got a veneer wall with a ventilation space vented to the soffit behind the brick.

  4. GBA Editor
    Martin Holladay||#4

    Joshua,
    Sorry for sending you to the wrong article. The air gap and the asphalt felt go a long way toward reducing the risk of inward solar vapor drive, especially if the air gap has openings at the base of the wall and the top of the wall to encourage air flow. If the air gap is clogged with mortar droppings, and it doesn't get much air flow, that's another story.

    Celotex Corporation manufactured many products over the years, including polyisocyanurate (rigid foam) and fiberboard sheathing. I'm not sure which Celotex product you are referring to.

  5. Joshua Van Tol.||#5

    我正在谈到的escotex是一个压制的灰泥膏药支持产品。它的钥匙被模制成一侧,另一侧相对光滑。奇怪的是,这所房子在外面的墙壁上有灰石体吸引物,在楼上的天花板上,但其他地方的传统车床。我只认为他们在当天拍摄了更好的气密性。

    我们已经完成了一些演示,我们看到差距并不是所有的插入砂浆粪便。砖砌形状非常好,裂缝或其他问题很少。

    So, would you say that if I created some weep holes at the bottom of the wall, I should be pretty safe if I wanted to install a non-vapor permeable insulation in the stud cavities? Also what about the idea of a thermal break on the inside? Would I risk problems with the framing then?

  6. GBA Editor
    Martin Holladay||#6

    Joshua,
    问:“如果我在墙壁的底部创造了一些哭泣的洞,如果我想在螺柱腔内安装非蒸汽的可渗透绝缘,我应该非常安全?”

    答:如果您担心内向太阳能蒸汽驱动,则非气相渗透绝缘将导致较少的问题而不是蒸气渗透绝缘。

  7. Joshua Van Tol.||#7

    马丁,

    是否有任何研究表明,在我所描述的情况下,在某种情况下在情况下经历了阳光驱动相关问题的可能性?如果我可以在不腐烂我的房子的情况下,我真的非常宁愿拥有封闭式电池绝缘的卓越的空气密封性和r-valual。

    I'm kind of inclined to go ahead with the closed cell plan, partly because I'm not sure how I'd contain blown insulation from going into the space between floors, given that this house is balloon framed, and does not have any blocking in the wall as near as I can figure.

  8. GBA Editor
    Martin Holladay||#8

    Joshua,
    The classic solar vapor drive problem involves a "reservoir" cladding (you have that), no air space or an air space that is compromised by mortar droppings (you don't have that), vapor-permeable sheathing (you have that), fluffy insulation that is both air-permeable and vapor-permeable, interior polyethylene, and air conditioning.

    If you don't have interior polyethylene, I wouldn't worry.

    显然,如果您能找到一种方法来安装喷雾泡沫或注射泡沫,您将不会有任何问题。

  9. Expert Member
    Dana Dorsett||#9

    "In an ideal world, we'd tear out the exterior walls, insulate full depth with closed cell spray foam, and then re-install drywall, perhaps with a layer of rigid foam under the drywall to reduce thermal bridging and bring the wall thickness up at least to the original thickness so that baseboards and such can be re-fitted."

    你打算胆无间的墙壁吗?

    There's nothing ideal about full depth closed cell foam. In fact the best you can do is about 1/4-1/2" shy of full depth because the stuff is so hard to trim flush with the studs, which means you end up with slightly more severe thermal bridging. Even at a theoretical full-fill the thermal bridging robs closed cell foam of nearly half it's performance potential, even in a balloon framed structure (about a 20% framing fraction typical. for 16" o.c. construction sans firestop blocking). Save the high R/inch goods for the thermal break layer where you reap the full value.

    Then there's the matter of the extremely high lifecycle global warming of closed cell foam blown with HFC245fa (almost all R6/inch or better foams used in the US are blown with it), at about 1000x CO2.

    And at 3+" the stuff has a permeance of less than 0.4 perms, which means there is effectively zero potential for drying toward the interior.

    如果你肠道墙上你没事1”的接近d cell on the interior (about 1 perm) as an air seal and semi-permable condensing surface, with the rest of the cavity filled with damp spray cellulose, or compressed batts, if you can be obsessive about perfect fit, rock wool preferred. Many 1920s homes were framed with full-dimension 2x4s that run between 3.8-4.2" in actual depth, which means even with 1" foam against the ship-lap you don't have to compress it much, but there may be non-standard width issues to work around too, which is why sprayed/blown products are a better choice. With ~R6 outside of ~R10-R12 of fiber you have a sufficient foam/fiber ratio for dew point control without needing to go low-permeance on the interior side- standard latex paint is good enough.

    If you're not going to gut it, blowing it full of cellulose at 3-3.5lbs density works. If the latter it's advisable in your climate zone to reduce the vapor retardency of the interior finish to something between 0.5-1 perms, which can be done with "vapor barrier latex" paint (about 0.5perms).

    In a full-gut situation you could cut in some 1.5" wide strips of 1/2"foil-faced polyiso glued to the framing edges as a thermal break before completing the cavity fill. If the center cavity depth from wallboard to your spray foam is more than ~3" nominal with the strips added it makes the center cavity R ratio a bit marginal, and a "smart" vapor redarder such as Certainteed MemBrain or Intello Plus would be called for. If you have the room for it go ahead and add more. With polyiso, at 3/4" you would be roughly doubling the R-value at the framing. You could also go for full sheets of polyiso on the interior,caulked to the framing and seams sealed with FSK tape and skip the smart vapor retarder. That would yield a modest improvement in whole-wall-R, but it would also eliminate any possibility of drying toward the interior, with a modest risk of summertime condensation inside the wall cavity. (That risk is pretty low if you vent the masonry cavity both top & bottom, and have 1-perm spray foam on the ship-lap.)

  10. Joshua Van Tol.||#10

    Dana,

    You've given me a bunch to think about. Thanks. I'm now leaning towards either the full sheets of polyiso or perhaps something like what I've shown in the attached image:

    图像中所示的方案的优点是喷雾泡沫可以在螺柱上圈出泡沫“帽”并形成连续层。我有足够的空间在没有问题的情况下加入1英寸或更多的泡沫。

  11. Expert Member
    Dana Dorsett||#11

    If you take the approach as shown in the sketch, use open cell foam trimmed flush with the caps, not closed cell, with vapor barrier latex on the wallboard. The cost will be much lower, the air tightness comparable or better, the difference in whole-wall R would be negligible, the greenhouse gas footprint about 10,000x lower, and you could skip the side-cap detail (just use 1.5" end caps glued/tacked in place prior to foaming.)

    If you went with full sheet iso instead of caps you can skip the v.b. latex, and the open cell foam would be easier to trim (otherwise you'd be nicking your end caps if your not careful.)

  12. Eric West.||#12

    I'm in roughly the same boat as Joshua, but in Climate 5B (cold-dry Denver, also not sure how big or open the air-space behind the brick is, I don't have any weep holes, so I still have some investigating to do.)

    Dana,
    If foam strips are added to the interior studs as you suggested, will 1" of CC spray foam against the sheathing with the balance of the space filled with damp-spray cellulose or fiberglass work?

    谢谢
    Eric

Log in or create an account to post an answer.