Hi,
What is the suggested minimum of closed-cell that should be sprayed under a roof deck in Zone 5?

My intent is to spray open cell over the closed to a total R-40. Thanks.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay||#1

    Consor,
    Here is a link to an article that will answer your questions:How to Build an Insulated Cathedral Ceiling.

    Briefly:

    1. According to most building codes, the minimum R-value of an air-impermeable insulation material installed on the underside of the roof sheathing (in your case, closed-cell spray foam) in Climate Zone 5 is R-20. That would require a little more than 3 inches of closed-cell spray foam.

    2. Once the spray foam has cured, you can install almost any type of insulation on the interior side of the closed-cell spray foam to make up the total R-value you seek. (R-40 may be allowed by your local building department, but R-49 or more would be better.) The insulation installed on the interior side of the closed-cell spray foam should be in direct contact with the closed-cell foam.