EPS foam density for use under concrete slabs and around stem wall
Hi everyone,
我正处于需要在住宅净零项目上为我们的平板基础 /茎墙购买一些EPS泡沫的时刻。过去,我已经阅读并发布了该项目,似乎有一个共识,即从两种应用中的抗压强度角度来看,II型EPS泡沫应该很好。
问题是制造商推荐IX型,因为它具有更令人印象深刻的抗压强度属性,他的建议是否对II型的住宅基金会工作有价值吗?我认为我会通过询问在没有销售偏见的现实世界中使用EPS的人们来验证他的建议
我们的粉底是一个4英寸的平板,有6英寸厚的茎壁,平板下方的3英寸刚性EP和茎壁外部外部的3英寸。例子:http://foundationhandbook.ornl.gov/handbook/images/Chapter%204/4-11_no-cap.png
The Type I EPS is rated at a compressive strength of 15-21 PSI, the Type IX is rated at 25-33 PSI. The manufuacturer I’m looking at is Insulfoam, data sheet is here:http://insulfoam.com/wp-content/uploads/2014/04/13001-Below-Grade-EPS-Overview-TDS-WEB-8-16.pdf
Any advice is much appreciated.
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
Replies
Joshua, for most situations, type 2 if fine for sub-slab use. Its compressive strength is similar to sandy soil. A 4" slab contributes about 50 psf of load; add a 40lb live load and you're still below 1 pound per square inch. The compression curve for foam plastic is usually pretty straight, so insulation rated at 15 psi would compress somewhere in the neighborhood of 0.015 of its thickness. For 3" foam, that's less than 1/16". Not enough to worry about.
9型更好的是支持屋顶上层载荷的区域,例如下面的地下。
迈克尔,
Thanks for your very helpful comment. I've decided to edit my article,“Choosing Rigid Foam,”to include your advice.
-- Martin Holladay
Joshua: Remember to look for reclaimed foam.
For almost all residential slab applications Type-II EPS is fine. But under footings or load bearing posts it may need to be something denser. EPS insulated concrete forms (ICF) are all Type-II, and it is sometimes quicker / easier / cheaper to pour the stemwalls in ICFs, unless you find a source for used roofing EPS, which is almost always Type-Il, to enable a "walkable" membrane roof. Type-I is too easy damager or to leave permanent boot tracks in, even though it's still strong enough once the slab is installed. With Type-II you can usually walk on the foam prior to the pour without screwing it up (unless you are a 300lb guy carrying 150lbs of rebar on one shoulder.)
商业建筑重新屋顶/拆除的收回EPS相当普遍且便宜,通常为1/4-1/3,从打捞服装和泡沫回收商中获得的Virgin Stock Goods的成本。它在那里,您只需要搜索一点即可。尝试搜索您的本地craigslist查看:刚性绝缘,例如:
https://boston.craigslist.org/search/sss?query=rigid+Insulation
https://denver.craigslist.org/search/sss?query=rigid+insulation
https://sacramento.craigslist.org/search/sss?query=rigid+insulation
Dana, you mention using reclaimed foam. How about factory seconds where the boards are not of uniform density? Some areas are very firm while others are spongey. Will those areas compress immediately as the slab is poured or will it result in later cracking from uneven settling?
For higher loads, see here:
http://www2.owenscorning.com/worldwide/admin/tempupload/pdf.077_HighDensity_E_1.pdf
感谢您提供的所有有用信息。我环顾四周,寻找了II型,在华盛顿州地区没有发现任何东西。有人有很好的来源吗?
华盛顿州涵盖了很多领域 - 您能更具体吗?(如果您住在奥林匹亚,您并不想从斯波坎运送它,但是Portand或Bellingham并非没有问题。)
Nationwide Foam ships anywhere (for a price based on distance from the depot), and has a depot within a day's drive of any WA location.
http://nationwidefoam.com/
We are building in Yakima WA.