ERV / HRV从炉子返回网络中抽取?
我有一个已经运作了一段时间的ERV,新鲜的空气在专门的跑步进入主起居区,但陈旧的皮卡未完成。问题是我所希望的贯穿实用追逐将非常紧密的工作(追逐装满了管道,管道,炉子进气和排气等),并且必须穿过两个楼层来启动。
阅读制造商的文档,他们的评论突然跳出来 - 他们说,通常空螺柱腔将用于该装置的RA(返回空气)。突然间点击了,如果我用渗透到炉子返回导管的ERV陈旧拾音怎么办?这不是我经常描述的一个方案,但是当管道既新鲜和陈旧到炉子返回全部时,就没有存在的问题。
在ERV户外排气时,我有一个后面的阻尼器,所以炉子不应该在断电时向ERV建立后来。唯一真正的担忧是:
1) Obviously the furnace return grilles are not located in the same places you’d ideally place ERV return grilles- but, it would be better than how it is today (a naked pipe end in the basement), and I could possibly cut an ideally situated new return grille into the existing furnace return network (with a damper to flow match)
2)当两者运行时,ERV都必须对抗炉扇进行空气。This is what I’m really here to ask about- the ERV is pretty powerful, and the 4 large furnace return grilles have a pretty gentle flow today, so intuitively I’d hope the network can trivially supply an extra 100CFM without totally killing the performance of the ERV. However, while I have an anemometer & manometer, I don’t know the math to work this out to be sure. I know the balance of the ERV would change, but it’s already set to draw more fresh than it exhausts stale, and exhausting a little less stale some of the time would improve the thermal scavenging performance anyway.
有人会评论吗?炉内全部典型的静压下降太荒谬了吗?有没有考虑的Gotchas?谢谢您可以提供的任何输入。
答案
测量您希望与炉扇一起连接的返回压力挡板中的压力在高速上运行。然后,您可以看看您的ERV的鼓风机曲线,并弄清楚该压力会使系统不平衡。
大多数通风鼓风机都设计成具有陡峭的压力VS流,例如在我的ERV上运行在0.4“水,如果我连接到额外的0.1英寸的管道,则减少了80到75 CFM的流量,这并不多。
我的觉得如果你的回报的压力降低0.1“,大多数ERV / HRV它不会显着影响平衡。如果是那么,我会寻找连接它的其他方式。你可以得到如果您在面向流动方向的弯管中添加肘部,请额外的额外帮助。
它会不平衡,但是多少取决于所涉及的压力和ERV中的风扇类型。连接到返回管道,并测量ERV流量的变化,无需炉膛运行。