GBA Logo horizontal Facebook LinkedIn Email Pinterest 推特 Instagram YouTube Icon Navigation Search Icon Main Search Icon Video Play Icon Audio Play Icon Headphones Icon Plus Icon Minus Icon Check Icon Print Icon Picture icon Single Arrow Icon Double Arrow Icon Hamburger Icon TV Icon Close Icon Sorted 汉堡/搜索图标

社区and Q&A

外部建筑/保温新家

Thierry Swinson|发布了General Questions

我即将开始建设3000平方英尺,1个1/2故事的房屋,在3A区(阿拉巴马州中央)。
The house will have a standing seam metal roof and a drilled pier foundation with open crawl space. Air handlers and ductwork will be above the first floor ceiling, on the back side of the second floor knee wall.

我目前的建筑/绝缘计划是:
– Roof: Metal roof / Ice & water shield membrane/ 7/16 OSB/ Closed cell SPF sprayed 5″ thick between 2 x 6 rafters
– Exterior Walls: Cement board siding / membrane / 1/2″ OSB / Closed cell SPF sprayed 3 1/2″ thick between 2 x 4 studs on 16″ centers / 1/2″ gypsum board
——底部弗洛or: Hardwood floor / 3/4″ T&G Advantech OSB / Closed cell spray foam sprayed 4″ thick between 2 x 12 joists

The builders I have talked with have concerns that the enclosure will be too air tight from the CC SPF. I intend to address this with a ventilation duct to outside air tied into the HVAC system. They are also concerned about trapped moisture causing the OSB and other wood to rot.

您是否会建议您的外部建筑/绝缘计划的任何变化?

GBA Prime

加入建设科学专家的领先社区

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay||#1

    Thierry,
    It's very difficult to install closed-cell spray foam at a thickness of 3.5 inches between 2x4 studs. Since this type of foam is so difficult to trim, you are more likely to end up with about 3 inches of insulation.

    是的,您需要通风系统。以下是一篇文章的链接,该文章解释了您的选项:Designing a Good Ventilation System.

    我不知道你计划在墙壁护套的外侧安装什么类型的“膜”。如果你的意思是透气的家庭包衣或沥青感觉,你会没事的。

    Your roof assembly is a type of assembly that makes it impossible for your roof sheathing to dry in either direction. Opinions differ as to how risky this approach is. If you want your roof sheathing to be able to dry out in at least one direction, you should create a ventilation channel between the top of your insulation and the underside of your roof sheathing. You can do this with a product like AccuVent or with site-built insulation baffles that are strong enough to resist the expansion pressure of the spray foam.

  2. Thierry Swinson||#2

    I was planning on closed cell spray foam in the walls (instead of open cell ) to get the higher R value. I understand your point about the difficulty in trimming the closed cell foam. Even if I only get 3 inches with the closed cell foam, the R value will still be around 18, whereas with open cell (which trims easier) R value is only about 13 for 3 1/2" thickness.

    If I used a product like the AccuVent between the roof sheathing and the CC SPF, would I need to provide a path for venting at the the top end near the roof ridge? Looks like air could come in from the bottom end at the eaves but would have no place to go unless the top end was also vented to outside.

  3. GBA Editor
    Martin Holladay||#3

    Thierry,
    The detail at the ridge is called a ridge vent. Any roofer you talk to will know what a ridge vent is.

    If you've never seen what a ridge vent looks like, just Google "ridge vent."