Minisplit for a small room

詹姆斯喜世|发布了Mechanicals

I’m considering a mini-split install in our house. I’m in Austin TX, so it’s a climate that requires significant cooling. I have calculated loads and I have questions about what happens if one has a mini-split running in a low load room. It’s a child’s bedroom and the doors are closed all night.

The room has internal walls on 3 sides and just one 3×5 window. Currently the load calc shows it at about 3300 BTU (of course that is at design temperatures of nearly 100°F and 72°F inside).

We’re considering using the new Mitsubishi ceiling mounted cassettes (that fit between 16 inch on center ceiling joists), the smallest of which are rated at 9,000 BTU. MLZ-KP09NA计画ps://nonul.mylinkdrive.com/item/MLZ-KP09NA.html我找不到最低容量,但承包商希望能够报告系统在MITSU软件中建模建模时。让我们假设它的折出比率为30%?

What should I expect from such a set up? My thoughts are that that means that at design temp it will basically turn-down to around 3000 BTU of cooling and thus run continually with low fan speeds.

What what about in shoulder seasons, the majority of the year when let’s say 1,000 BTU of cooling is needed? It would cycle on and off frequently, right? I’m concerned about noise (on/off, although I’m assured that it’s barely audible), swings in temperature and inconsistent fan speeds.

Another concern would be humidity removal, but I do plan to have a dedicated dehumidifier in the house (UltraAire 90H probably), so I’m not really relying on the AC for dehu.

The alternative would be a ducted mini-split to service two bedrooms and a bathroom, combined loads of about 9,000 BTU at design conditions. The downside of that is:

– unit and ducting would have to be in the unconditioned attic (whereas ceiling mounted cassettes can be covered with blown-in insulation)
– noise transfer from ducting
– lack of zoning.

I could ameliorate the hot attic unity/ducting by doing a fur-up (“reverse bulkhead”) in the attic, which is possible, but a fair amount of framing, air-sealing, and insulation work. I’d do that, though, if I thought that a very oversized mini-split unit was going to cause big comfort problems (not so much concerned about efficiency here, sadly).

GBA Prime

加入建设科学专家的领先社区

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay||#1

    James,
    I think that the simplest solution is to install a window-mounted air conditioner. Instead of mounting it in the window, though, build a sleeve through the exterior wall that is sized for a small air conditioner. The cost is low, and you can buy a right-sized unit.

  2. 詹姆斯喜世||#2

    Yes, then one could match capacity. But:

    - Walls are CMU block, so the sleeve would be a difficult install.
    - Noise is substantial (although the child does have a white noise generator ...)
    - Aesthetic concerns

    I'm still interested to know what happens when a mini-split is oversized, anyone got experience there?

  3. 肖恩·丁特||#3

    Don't they have multi-cassette units with the single condenser? Multizone condenser running 2-3 heads? That just has the refrigerant lines (and condensation evacuation) which can be better insulated through an attic, right?

    Perhaps something like this:计画p://www.tamtech.com/return-air-pathways如果你有邻墙空间或愿意削减into the door - effectively vented the room air out into the hall or larger house itself?

  4. vantful.||#4

    Generally it will short cycle (turn on and off) instead of modulating once it gets below the minimum Btu output. On the cooling side this lends itself not lowering the humidity effectively and increased energy usage

  5. Expert Member
    Dana Dorsett||#5

    当迷你拆分超大时,它以最小速度进行大量循环开/关,在下面的额定效率下运行。他们仍然非常安静,舒适 - 大多数比你的冰箱更安静。在某种程度上超大,他们必须在“干燥”或“Dehumidify”模式下,大部分时间都在TX气候中的潜在负荷领先地步。

    I think MLZ-KP09NA cassettes are designed only for use with multi-split compressors, not it's own dedicated outdoor unit (?). (They only have a submittal sheet for the multi-zone configuration.)

    Better-class half ton PTAC or PTHP units with scroll compressors can be pretty quiet at low speed too, but it sounds like you don't want to deal with the wall-sleeve issue.

  6. 詹姆斯喜世||#6

    Thanks all. I forgot to mention that this would be part of a multi-zine system, probably 5 or so of these heads.

    But I get the message. Too much oversized means cycling on and off. Bad for efficiency but not terribly noisy. Eventually causing issues with humidity removal.

    The trouble, as has been discussed around here a little, is that mini-splits with closed doors in a cooling climate are problematic. In a heating climate it’s ok, good even , to have th bedrooms a few degrees lower than the rest of the house. But in a hot humid climate you really want the opposite, the bedrooms more conditioned (less hot). But then you run into a small version of the smallest system have too much capacity.

    I’m hoping that the mitsu multi-zine layout software gives us a clear indication of minimum capacity at each head. Then we can decide between ducted mini-split and head in each bedroom.

  7. GBA Editor
    Martin Holladay||#7

    James,
    您描述的问题有两个标准解决方案(“卧室负载对于MiniSplit Head太低”):

    1. Install a ducted minisplit that serves multiple rooms.

    2. Install a conventional forced-air duct system connected to a split-system heat pump / air conditioner.

  8. 詹姆斯喜世||#8

    谢谢!今天三菱人们的一些词,头部本身可以拨到1,000岁以下的BTU,但这一切都取决于哪些压缩机以及其他头部正在呼唤什么。例如4吨外压缩机可以一直拨到6K BTU,所以只要其他头部正在采取5k容量,那么那间房间可以做到〜1k。可能会在较小的外部压缩机上获得更低的要求。

    Basically the answer requires running a few designs through the "System Builder" software and making assumptions about what other heads would be doing (which in our case with high thermal mass, a dog in the house at all times, thus no real set back opportunities will be fairly easy). When that's complete I'll try to follow up with the documents.

    I'm trying to avoid ducting in the attic!

  9. Expert Member
    Dana Dorsett||#9

    It's good to know that the cassettes will modulate with load on a multi-split whenever they can, and that the -KP09 can throttle all the way back to 1000 BTU/hr, which is GOOD.

    The whole house cooling load is likely to be above the 6000 BTU/hr minimum much of the time, which means the micro-load of the bedroom would still be reasonably served with most or all of the other zones modulating on their loads.

  10. Expert Member
    阿科斯||#10

    I had to deal with a similar cooling issues (LG 9000btu head in a small room). It does work just be careful with placing the outlet. I find that even on the lowest setting there is too much airflow across the bed which can get uncomfortable. Never had issues with short cycling (usually have more than one zone running at night time).

  11. Jon R.||#11

    I interpret the Mitsubushi comments to mean that the head/cassette cannot modulate - it's on or off and how many BTU depends on what other heads are on and how big they are. Ie, hard to predict how the refrigerant flow will be distributed. You might sometimes get 1K BTU (or less) - but sometimes 6-9K BTU.

    这同意了我所期望的多裂分(VS一个每个头部可以调制的VRF系统)。

  12. user-7653783||#12

    James,

    I’m thinking about doing a similar thing with a 9kbtu MLZ cassette in three bedrooms even though the bedroom heating and cooling loads are significantly less. I like the ability for each room to have their own zone and temperature control. I’ll also have another 12k cassette for the first floor.

    How did the 9kbtu mlz work in the low load room in your case?

    I realize my results may depend on what the other heads are calling for, but I’m interested in hearing how the oversized cassette in a small room as part of a multi split is generally working.

    Thank you

    Greg

  13. Jon R.||#13

    NEEPsays that MINIMUM speed cooling capacity should be <= 115% of design cooling load.

    The comfort and efficiency effect of being near this limit is very equipment dependent and rarely quantified.

    Less than design load latent performance is usually poor, even when rated capacity equals design load. Install dehumidification.

  14. user-7653783||#14

    Thanks Jon. That link is very helpful. I read it and will explore that website further.

    一个问题 - 当他们谈论最小速度冷却能力<= 115%的设计冷却负荷时,它们是参考室外单位的最小速度冷却能力和所有房间的设计冷却负荷的<= 115%,正确?