隔离小阁楼的经济方式

BAC478|Posted inGreen Building Techniqueson

我的房子前部有一个小的8×12入口。上方的阁楼空间可以从二楼访问。我想将其用作条件存储空间。
当我在肠道康复期间从after子上取下覆盖物和绝缘材料时,我注意到阁楼北侧的护套的上半部分是湿的。我相信这是由凉爽护套表面上的内部空气凝结的水分引起的。我认为南侧的太阳能加热足以使护套在白天的露点上方,并摆脱夜间凝结的水分。由于除去了绝缘材料,因此即使在雨期和下雨后,护套也不再湿,排除了屋顶泄漏的可能性。
afters是2×4。我打算用2x3绑住它,以增加绝缘深度。单山墙端的总屋顶甲板区域约为150平方英尺。我得到的报价约为5.5英寸深的闭孔泡沫,价格约为5美元/平方英尺。我无法在屋顶甲板上方添加泡沫面板,因为这条小入口的山脊仅在房屋其余部分的屋檐下(垂直)。加入屋顶甲板会导致两个屋顶仅在山脊附近相交,我认为这看起来真的很奇怪。
Is there a more cost effective way to insulate this small area? air permeable insulation means I have to vent the assembly which chews up insulation depth. I don’t want to add more than 1.5″ to the existing 2x4s because it decreases attic space. This is not enough area to rent the cellulose machine again, at least not in my opinion (I probably should have done this when I blew-in the rest of the second story, but I hadn’t discovered the problem yet)
建议?

GBA Prime

Join the leading community of building science experts

成为GBA Prime成员,并立即访问该领域的绿色建筑,研究和报告中的最新发展。

答复

  1. GBA编辑
    Martin Holladay||#1

    布莱恩,
    考虑到您列出的局限性,我认为喷雾聚氨酯泡沫是您唯一的选择。

    (By the way, your explanation of the damp sheathing on the north side of the roof was clear and accurate. It's fairly common for gable roofs to have damp sheathing on the north and dry sheathing on the south, as you observed, due to the beneficial effects of the sun.)

  2. 专家成员
    达娜·多塞特(Dana Dorsett)||#2

    有了2x4s + 2x2s,您总共有5英寸。屋顶甲板完全受到闭合泡沫的1英寸的保护,但几乎所有到处都有2英寸。可以安全地涂在一个通行证中的最大深度是2英寸,通过两次通行之间的冷却期,您可以在那里停留。

    If you give it a 2" shot of foam and fill the remaining 3" with a compressed R13 batt it will have nearly the same performance as a full fill of closed cell polyurethane.

    如果您没有2x2s,则使用1.5英寸Polyiso的after边缘带并填充压缩板将超过5.5英寸的闭孔泡沫的性能。

    You don't state your location, but with 2" of foam and a compressed (to ~3") R13 you would have sufficient dew point margin at the foam/fiber boundary even at the warm edge of US climate zone 7. In climate zone 4 or lower you'd be fine with 1" closed cell foam and a compressed R20 (or R19, if you're REALLY cheaping out.)

  3. BAC478||#3

    Old house, so true 2x4s. 4+1.5=5.5in. Closed cell is rated at about R7/in. fiberglass is about R3.6/in. I'm going to ask the obvious question: 7*5.5>7*2+3.5*3.6 so how will the foam+fiberglass have equal performance to full thickness closed cell? Unless we are talking moisture (or lack thereof) performance?

    Climate zone 5, zip 01301.

    不幸的是,泡沫和同等量仅在200 bf和600 bf尺寸中出现。我需要2英寸大约300英寸。一个600 bf套件在600美元的北部。我更喜欢摇滚羊毛,而不是玻璃纤维,这将增加$ 120。这使我回来了720美元,$ 750让有人喷洒它。玻璃纤维是50摇滚羊毛的成本%,这将使我的价格为660美元,仍然相对接近750美元。

    如果我用2x3水平绑扎墙壁,我将通过我决定使用的任何隔热材料来获得很小的热桥,并且不必担心在螺柱上通过1.5英寸的刚性固定。

  4. GBA编辑
    Martin Holladay||#4

    布莱恩,
    我认为达​​纳的观点是,穿过after子的热桥接往往会对这种类型的屋顶组件的热性能产生强大的影响,因此喷雾泡沫的热优势远低于大多数房主和建筑商的假设。

    这是您房屋入口处的一个小屋顶;不要过度思考。我认为便利和成本是重要的考虑因素,因此您可以根据这些标准选择方法(只要您遵守此处概述的基本建筑科学规则:如何建造绝缘大教堂的天花板)。