刚性泡沫爬行空间绝缘 - 蒸气渗透?
我们目前有一个18×30的爬行空间,在地板托梁上发泄了搭配薄塔绝缘。爬虫空间还连接到22×30的完整基底。在爬行空间和用胶合板封闭的地下室之间有一个2'x2'开口,以及用于导管的几个开口。爬行空间地板上安装了氡气缓解系统,塑料覆盖物在爬行空间墙上上升约10英寸。HVAC供应和返回,加热管道都通过爬行空间到房屋的那段部分。它周围有BATT绝缘,但在地方摔倒了。
We live in SW Ohio, Climate Zone 5 and it is usually pretty humid during the summer months. During the summer, the basement will get up to 65% RH and we get a bit of a smell that tells us it is time to turn on the dehumidifier. In addition, we are dealing with mice in the crawlspace and probably other areas as well. Also have lots of spiders.
For the winter I sealed up the two vents (can spray foam/rigid foam) with a plastic vent cover. I put plastic between the spray foam and rigid foam to pop it out if needed later. With the mice, needing to do some plumbing in the bathroom, my thoughts were to pull the batt insulation and use rigid foam on the crawlspace walls.
My initial thought was to use either Thermax or John Manville’s CI Max since both have the thermal barrier built in. But reading Info-512 on buildingscience said the perm ratings are too low and I may have issues moisture buildup between the concrete foundation wall and the rigid foam. I’m not sure if the thermal barrier is code in my area, but wanted to use it to be on the safe side.
John Manville安装说明可以选择使用连接到墙壁的1x毛茸茸条带以及附接到毛皮条带的泡沫板。这将留下一个小气隙,〜3/4“,可以缓解墙壁和泡沫板之间的水分的潜在问题吗?虽然冷基础墙可以诱导冷凝?你会密封泡沫板的顶部吗?
要么if a thermal barrier isn’t needed, go with the regular XPS? Seems like polyiso’s foil facing has the same perm rating as the thermal barrier versions and would still lead to the same problems.
想法?
Thanks!
HD
答复
HD,
没有理由的是,潮湿的混凝土墙需要“呼吸”或弥漫湿润的水分朝着家的内部。混凝土可以永远保持潮湿,而不遇到任何问题。低于级别的混凝土墙总是潮湿;这是他们的本性;所以你想防止对内饰的干燥,不鼓励它。毕竟,为什么邀请水分进入你的房子?
布鲁里溃疡建筑公司使用科学建议ilders that concrete basement walls had to dry to the interior. I opposed this advice for years, and Joe Lstiburek finally conceded, admitting that the advice was wrong. Read more here:Joe Lstiburek Discusses Basement Insulation and Vapor Retarders。
有关如何隔离爬行空间墙的良好建议,请参阅本文:建立一个不经常的爬行空间。
谢谢马丁,很高兴获得更新的信息。我读过“构建一个不辩营的爬行空间”,并对蒸汽屏障有一个问题。
“安装耐用的蒸汽屏障 - 例如,一个20密耳池衬里或Tu-Tuf poly - 在地板上,伸出爬行空间墙,到墙顶的3英寸内。留下3英寸 -墙顶的宽白蚁检查条带。“
我们的爬行空间地板中的当前被动氡减缓塑料仅抬起一英尺。如果我应该在墙壁上添加更多的蒸汽屏障并重叠,或者只是继续前进并加入刚性泡沫并跳过这一步?
再次感谢,
HD
HD,
问:“目前我们的爬行空间地板中的无源氡气缓解塑料左右。如果我在墙上增加更多的蒸汽屏障并重叠或者只是继续前进并加入刚性泡沫并跳过这一步骤?”
A. Just add rigid foam to the walls. The rigid foam is a vapor retarder. Installing polyethylene under the rigid foam is an optional step.