GBA Logo horizontal Facebook LinkedIn Email Pinterest 推特 Instagram YouTube Icon Navigation Search Icon Main Search Icon Video Play Icon Audio Play Icon Headphones Icon Plus Icon Minus Icon Check Icon Print Icon Picture icon Single Arrow Icon Double Arrow Icon Hamburger Icon TV Icon Close Icon Sorted 汉堡/搜索图标
社区and Q&A
Insulating an old farm house
瑞安骑士|发布了General Questions在
We bought a 111 year old farm house in northern Michigan 12 years ago. When we moved in, it did not have any insulation. Over the years, we’ve blown in cellulose into the wall cavities and roof and replaced the windows. A builder-friend also recommended placing 1 inch polyisocyanurate foam with foil on the inside wall just behind the drywall. We have followed this recommendation as we have renovated room by room. This year we are going to tackle the outside and replace the rotting/damaged original siding. I would like to add 1-4 inches of staggered foam on the outside as well but can I? From the reading I have done, I am fearful that there will be moisture buildup in the walls because it will not be able to dry to the inside. Local builders have told me everything from “don’t do it” to “it’ll be just fine” to “apply 1 inch of XPS foam and tape the seams”. Suggestions?
加入建设科学专家的领先社区
  1. GBA Editor
    Martin Holladay||#1
    Ryan,
    I think that this is a judgment call, and that your decision should be based in part on the condition of the wooden components that you inspect when the siding is removed.
    If everything is bone dry, I think that you can safely install several layers of rigid foam on the exterior side of your wall sheathing. Make sure that the R-value of the exterior rigid foam is enough to keep the wall sheathing above the dew point during the winter. That's going to take some figuring, because you'll need to add up the R-value of the cellulose and the interior foam, and aim for enough exterior foam to end up with the right percentage of exterior foam for your climate zone. For the concepts behind the calculations, seeCalculating the Minimum Thickness of Rigid Foam Sheathing.
    If your wall has rot or signs of moisture problems, it's time to rethink the idea of exterior rigid foam until you figure out what happened.
    Of course, it's always safe to install exterior mineral wool, because mineral wool is vapor-permeable. For more on this approach, seeWrapping an Older House with Rock Wool Insulation.
  2. Expert Member
    Dana Dorsett||#2
    使用未公开的EPS而不是XPS将为您提供更高的外部R,然后在其对外部的干燥速度被严重冲动。在2英寸/ r10,大多数XPS将在0.5-0.7的烫发之间运行,这良好地进入II类蒸汽迟滞。在3“/ R12.6 1.5LB密度”II型“的EPS将仅在1倍率下进行。1LB Type-I EPS(约R11.8 @ 3“)将运行约1.5次烫发,超过2倍的R10 XPS的干燥速率。
    At 1" XPS is typically ~1.2perms, give or take, but only R5, not much dew point control against an R15-R20 interior-side R.
    Are you in the U.P. (mostly US climate zone 7), or on the main part of MI, zone 6? In zone 6 a 3" layer of ~ R12 EPS is sufficient dew point control for up to R23 or so on the interor side of the sheathing. (Say 4" of cellulose + 1.5" of interior side polyiso.)
  3. 瑞安骑士||#3
    Thank you for your expertise Martin and Dana. We are in zone 6 just bordering 7. I'll pass the information on to our builder.